Post by mvitalis on Dec 5, 2012 13:16:40 GMT -6
I have a FloorStat 500650-120B; the Test button just started coming on during a heat cycle recently. No GFI message appears. The GFCI tests normally.
The light will not go out by setting to Standby. The only way to reset is to recycle power at the breaker. The light will remain off until some future heat cycle (unpredictable which one, but usually several go by); once on, it never resets until I recycle the breaker.
The unit appears to work normally whether the Test light is on or off. No additional messages are on the display.
Should I be afraid, or very afraid?
The unit is S# P0264219-1 dated 2006-12.
Thanks,
Maynard
|
|
|
Post by Christopher on Dec 6, 2012 7:44:28 GMT -6
Hey Maynard. The GFCI light acting like that is a good indication that the actual GFCI inside the stat is starting to fail. At some point it will probably actually start tripping, cutting power to the floor, and then eventually it will just get stuck closed. It's probably a good idea to start planning to replace it.
|
|
|
Post by mvitalis on Dec 6, 2012 11:30:52 GMT -6
Thanks.
Is it possible just to replace the GFCI inside the stat or do I have to replace the whole unit (which looks like it might be expensive)?
And do I just call your 800 number to get pricing and availability?
|
|
|
Post by Christopher on Dec 7, 2012 7:27:58 GMT -6
You'll have to replace the whole thermostat. The easiest way to do that would be to pop on in to Home Depot and get one there. If they don't have any on the shelves, they can order it, or you can just buy it from their website.
|
|