Post by geoguy on Dec 15, 2009 15:35:20 GMT -6
Could someone translate the "Euro-geek speak" installation parameters to "HVAC English-speak"? Or as Will Rogers would have probably said, "I have never met a customer who likes this thermostat." I could also add I have never met a service tech or installer who does either. I am particularly interested in Cy, bp, J7, and Cp.
|
|
|
Post by Jeremy on Dec 17, 2009 15:34:31 GMT -6
Hey geoguy! Thanks for posting. Most people have issues with those particular settings. I've attached a document to help explain those parameters. The proportional integral settings affect how the stat determines when to call for heat. We typically recommend to leave these at the default settings. However, some of the stats leave the factory with a Cp setting of 10.8. This needs to change to 3.6. Let us know if you have more questions. Thank you! Jeremy Wilson Attachments:
|
|